All hinges on the answer to one question: Is the service disconnecting means to be at/in MS or SPB?
Agreed.
GFP or GFI?
230.95 is your friend. That section has what you need.
All hinges on the answer to one question: Is the service disconnecting means to be at/in MS or SPB?
Not just the descriptor, but what the symbol represents.No.
Some of the debate has been on the descriptor (GFI, GFP, or simply GF) to use not its function.
...
The 10 conduits confuse me, but I've never designed an isolated phase installation. 3 phases and a neutral each with two conduits equals 8 conduits. It looks like the ground conductors are in their own conduits.
Is it correct to put the grounds in 2 separate conduits? It seems like they would be installed in each conduit with phase conductors. And do you really need a ground that is the same size as the phase conductors?
Every conduit needs a full sized equipment grounding conductor, if you are using an EGC wire. For a 4000A breaker, that is 500 kcmil.
Strange. 50 years of installing/inspecting service conduits and I never saw the need![]()
So a parallel EGC does not function the same as parallel ungrounded?I think the concept is that if there is an unintended connection of an ungrounded conductor with the grounding conductor in a raceway, all of the fault current available will flow through the lone grounding conductor in that raceway and you want enough of a low impedance to clear the upstream protection.
So a parallel EGC does not function the same as parallel ungrounded?
So a parallel EGC does not function the same as parallel ungrounded?
According to accessible archived info on nfpa website, first appeared in 1971 Technical Committee Reports. There is no substantiation provided in these 'reports'.... Unless someone wanted to research the ROP/ROC, we may never know the real reasoning behind it.
Anyone know how far back does this rule go?
...
Supposition borne of reasoned speculation my dear sir.Good question.
A parallel EGC does function the same as parallel ungrounded wires when things go right, but not when things go wrong.
The parallel sets are only placed in contact when they terminate at equipment. The sets are not in contact in the middle of the conduit run. Therefore, the ground wires among each conduit cannot share the fault current, if a fault occurs in the middle of the run.
If there is a fault from an ungrounded conductor onto its grounded conductor, occurring in the middle of the conduit, then most of the current will bypass the load, and travel on this particular set's faulted path, to take a path through the EGC back eventually to the source. The EGC in each parallel set needs to be able to carry current for enough time to trip the OCPD and clear the fault before it overheats and therefore melts.
Supposition borne of reasoned speculation my dear sir.![]()
I realize Mr. Soares is revered as an authority on the subject of grounding. So are we all to just take his word for it? Where's the proof? (I do not have the book). I am currently looking at it like Obama vs. Obamacare.The concept, of a fault occurring in the middle of a run, is actually put forth in Soares Book on Grounding, (chapter 9 page 133, in my 7th edition).
I realize Mr. Soares is revered as an authority on the subject of grounding. So are we all to just take his word for it? Where's the proof? (I do not have the book). I am currently looking at it like Obama vs. Obamacare.
Whether substantiated or not is moot. Code requires it, so we do it. :dunce:
Every conduit needs a full sized equipment grounding conductor, if you are using an EGC wire. For a 4000A breaker, that is 500 kcmil.
Isolated phase installations are, in my opinion, not recommended at all. The isolated phase will magnetize the surroundings, and these magnetic fields will get amplified if there is any ferrous conduit.
You are permitted to do isolated phase installations, given that all conduits take close paths so that the magnetic fields eventually get cancelled, and if you use non-ferrous conduit. Such as aluminum, stainless, PVC, LFNC, and others. Most people route the conduits along close paths anyhow.
I realize Mr. Soares is revered as an authority on the subject of grounding. So are we all to just take his word for it? Where's the proof? (I do not have the book). I am currently looking at it like Obama vs. Obamacare.
Whether substantiated or not is moot. Code requires it, so we do it. :dunce:
So both the number of conduits, and the number of conductors in each conduit are shown incorrectly on the posted one line.
If it were my choice, I would standardize on 500 kcmil Cu for this application. That would be 11 parallel sets, assuming that this is sized as an ordinary feeder. Each set would consist of a 3 1/2" conduit, and 5 qty 500 kcmil Cu conductors.
So both the number of conduits, and the number of conductors in each conduit are shown incorrectly on the posted one line.
Utilities often limit us to ten sets from a transformer.