The incoming 12kV overhead line enters a switch. Their is one 4" conduit that has only 3 #1/0 conductors in it leading to a 1500kVA. 1500*1000/12k/1.73=72A per phase. I should be using Table 310.77, #1/0 Type MV-105 rated for 5k-35kV. That puts the #1/0 at 215A. Well over sized. Run is only 500'. 1st question, am I using the right table? Second, why not use a smaller conductor since this is rated for well over the need?
The 12kV switch has another one 4" conduit with 3 #4/0 conductors in it leading to a 2500kVA. That equates to 120A per phase. Same table, derating does not apply, #4/0 is rated for 315A. Why are they now using an even bigger rated conductor for the 2500kVA? Couldn't we just use a #1/0 for this as well? Please explain to me what I am doing wrong or not understanding. Thank you.
The incoming 12kV overhead line enters a switch. Their is one 4" conduit that has only 3 #1/0 conductors in it leading to a 1500kVA. 1500*1000/12k/1.73=72A per phase. I should be using Table 310.77, #1/0 Type MV-105 rated for 5k-35kV. That puts the #1/0 at 215A. Well over sized. Run is only 500'. 1st question, am I using the right table? Second, why not use a smaller conductor since this is rated for well over the need?
The 12kV switch has another one 4" conduit with 3 #4/0 conductors in it leading to a 2500kVA. That equates to 120A per phase. Same table, derating does not apply, #4/0 is rated for 315A. Why are they now using an even bigger rated conductor for the 2500kVA? Couldn't we just use a #1/0 for this as well? Please explain to me what I am doing wrong or not understanding. Thank you.