I've been studying to take my exam for the last 6 weeks or so and I have a question that's been bothering me.
It's my understanding that you size a motors thermal overloads based on nameplate amperage if provided. If not, you use the FLC tables. Then based on that figure, you can correctly size the heaters per 430.32.
Based on the FLC values, you add 125% of that value to get the ampacity needed for your branch circuit wiring. Then depending on your overcurrent protection choice, you multiply the FLC value by either 175%, 250% to obtain your overcurrent protection for short circuit, ground-fault protection. (T430.52)
Example:
Branch circuit feeding a single phase, 2hp, 115V motor.
FLC current = 24 amps.
Heater size = 24 * 1.15% = 27.6 min 24 * 130% max = 31.2
OCPD = 24 * 250% = 60amp (inverse time breaker)which happens to be a standard size.
Here's my question: From the OCPD, you are allowed to run size 10awg THHN which is good for 30amps but what happens in the event that the heaters short out or become faulty? Then in theory the motor can go into Locked Rotor Current and the next device set to trip would be the breaker set at 60amps.
How is it that you can have size 10awg wire leaving a 60amp breaker? Am I correct that the only way that motor will pull more than 24amps is if it goes into Locked Rotor condition? At which time, the current will far exceed 60amps in turn tripping the breaker and protecting the conductors??
Thanks.
It's my understanding that you size a motors thermal overloads based on nameplate amperage if provided. If not, you use the FLC tables. Then based on that figure, you can correctly size the heaters per 430.32.
Based on the FLC values, you add 125% of that value to get the ampacity needed for your branch circuit wiring. Then depending on your overcurrent protection choice, you multiply the FLC value by either 175%, 250% to obtain your overcurrent protection for short circuit, ground-fault protection. (T430.52)
Example:
Branch circuit feeding a single phase, 2hp, 115V motor.
FLC current = 24 amps.
Heater size = 24 * 1.15% = 27.6 min 24 * 130% max = 31.2
OCPD = 24 * 250% = 60amp (inverse time breaker)which happens to be a standard size.
Here's my question: From the OCPD, you are allowed to run size 10awg THHN which is good for 30amps but what happens in the event that the heaters short out or become faulty? Then in theory the motor can go into Locked Rotor Current and the next device set to trip would be the breaker set at 60amps.
How is it that you can have size 10awg wire leaving a 60amp breaker? Am I correct that the only way that motor will pull more than 24amps is if it goes into Locked Rotor condition? At which time, the current will far exceed 60amps in turn tripping the breaker and protecting the conductors??
Thanks.