BJB48
Member
- Location
- Hanover, PA
I am working on a methanol installation for a waste water treatment plant. Installation consists of a 4000 gallon tank, methanol feed pumps, sump pump, leak detection equipment etc. The tank and metering pumps and sump pump are located on a concrete slab. All pump VFD's, leak detection, truck grounding for fill station was relocated to a separate slab that will have an bus stop type roof and walls around all for the pump panels. Engineer specified a 10' boundry for class 1 div 1 from sump pump and metering pumps. All conduits into and out of area are PVC with 6"+ of concrete encasement more than 24" below finish grade. Transistion from PVC to PVC GRC is 2' below top of concrete. We planned on seal offs 12" above top of concrete for all conduits to equipment within the Class 1 Div 1 area. The rack's for the VFD's,etc. on the remote slab are a minimum of 12'6" from the closest conduit stub up in the classified area. County electrical inspector citing 514.8 and 515.9 says seal offs are required on both ends of the conduit runs. I contend that the single seal off within the classified area meets the 10' rule from boundry and is all that is required per 501.10. Any thoughts would be greatly appreciated.
Thanks,
Bruce
Thanks,
Bruce