Installer
Senior Member
- Location
- DesMoines, Washington
I'm very rusty on Electrical Design . I'm trying to redesign an existing electrical service.
I have a 2 wire 208 feed coming from a 3 phase breaker on 208Y/120 3 Phase 4 Wire Panel through an old conduit.
I'm stuck with what I have, which is 2 Hots and a Neutral.
For some reason, I am thinking I should be getting 2 Hots and a Ground, but what I have is 2 Hots and a Neutral.
I'm using a 3 KVA ACME T-2-79743-S Transformer.
I have some questions about the one line I developed.
1. Is it generally connect?
2. Do I place the Disconnect Switch prior to or after the Transformer? Does the NEC specifications
for a Separately Derived system govern this?
3. Do I tie the Neutral to the Ground at the Counterpoise ( see red circle) Does the fact that I have 2 H,1N vice 2H 1G make a
big difference
Thank you in Advance