That I agree with..................I think 480 is twice 240. Again, math is hard.
That I agree with..................I think 480 is twice 240. Again, math is hard.
230V is live and neutral. 400V is generally 3-phase.Certainly within each wye system, the L-L voltage is 1.732 times the L-N voltage. That's expressed in the nomenclature 415Y/240, that means a wye system with 415V L-L and 240V L-N.
So the UK has 415Y/240 (as I understand it, or 400Y/230 nominal for EU harmonization). The US has 208Y/120. The US system is half the voltage of the UK system, for L-L or L-N or any corresponding measurement.
Now how about my question, is it common to have 2-wire 415V (or 400V) loads in UK/Europe? Here it is not uncommon to have loads that are designed for 2-wire 208V, which can be run L-L on a 208Y/120 system.
Cheers, Wayne
Glad we can agree on that.230V is live and neutral. 400V is generally 3-phase.
Good!Glad we can agree on that.
So in the UK, if a building is supplied with 400V 3-phase power, does the supply typically have a neutral as well? Allowing the use of 230V 2-wire loads, from L-N?
Second question, when 400V 3-phase power is available, how common is it to have a 2-wire load that works on 400V, supplied L-L?
Cheers, Wayne
Isn't a single-phase load a 2-wire load?I don't recall 2-wire loads. Just single phase or 3-wire.
Called live and neutral in my neck of the woods.Isn't a single-phase load a 2-wire load?
Aren't all 2-wire loads single-phase?
You never have 2-wire live-live loads?Called live and neutral in my neck of the woods.
Well, I didn't. We had live and neutral 230V and 400V 3-phase. I can't for certainty that no one did. But my background was/is industrial power electronics so we didn't have live-live.You never have 2-wire live-live loads?
Cheers, Wayne
And if you connected something between only two of the ungrounded lines it is still a single phase load but with 400 volts applied.It is just single phase for 230V. Not single phase.
He never said 240Y he said 208/120 is half of 215/240 (really should have said 216/240, but then multiply or divide any whole number by square root of three and you not very likely to have a whole number result...I think 120 is twice 240.
But 240Y is NOT 415V
Is what is at the load end of the 950 foot run still in same building? You may actually have more options if it is a separate building/structure than if it is in same building.Thank you INFINITY. I don't know transformers that well.
What am I missing?
1. Please remember I am stuck with 2 Hots and 1 Neutral conductor because its a direct bury under a busy area.
2. The Neutral is coming from the Neutral bus that is bonded to the Ground bus at the Panel.
3. I tied the Neutral to the Ground at the Counterpoise at the Site. (red circle)
4. What am I missing?
Thanks for your help View attachment 2557349
415.0 / sqrt(3) = 240.208/120 is half of 415/240 (really should have said 416/240, but then multiply or divide any whole number by square root of three and you not very likely to have a whole number result...
Rounded results. Get enough places to the right of the decimal (in all the figures used) and the results get closer to one another.415.0 / sqrt(3) = 240.
240.0 * sqrt(3) = 416
Is there an applicable standard which defines whether the nominal system is defined in term an integral L-L voltage or an integral L-N voltage?
Cheers, Wayne
Correct, that's my point.Rounded results. Get enough places to the right of the decimal (in all the figures used) and the results get closer to one another.
True.Correct, that's my point.
So your saying that it should be 416/240 instead of 415/240 is equivalent to saying that the L-N voltage is the starting number, with L-L voltage derived by multiplying by sqrt(3). As opposed to the L-L voltage being the starting number, with the L-N voltage derived by dividing by sqrt(3) (in which case both 415/240 and 416/240 are valid options).
Cheers, Wayne
Bottom line, all wye systems have line to line voltage that is square root of 3 times higher than line to neutral voltage.UK and other European countries are 400V/230V. Nominally.
Absolutely you DO!Except it isn't. There is no 120-0-120 for a start, We have 0-230V. And no 208V or similar.