I think that what Jraef is saying is that if the primary is 1Ø, 480 volts you don't have much of a choice but to use a 2 pole breaker in the 3Ø panel.
 
I think that what Jraef is saying is that if the primary is 1Ø, 480 volts you don't have much of a choice but to use a 2 pole breaker in the 3Ø panel.

You can use a three pole breaker but you ultimately only utilize two lines from the source.;)
 
You can use a three pole breaker but you ultimately only utilize two lines from the source.;)

Very true but the OP did specifically ask about a 2 pole. I'm guessing that maybe he's concerned about an imbalance of some kind.
 
Very true but the OP did specifically ask about a 2 pole. I'm guessing that maybe he's concerned about an imbalance of some kind.
Which is unavoidable other than to compensate by balancing any other single phase loads accordingly if possible.
 