Single phase disconnect for 120V motors

Status
Not open for further replies.

mshields

Senior Member
Location
Boston, MA
I'm doing a project that will require a couple dozen branch circuits to 1/2HP overhead doors. Each is 120V, 9.8A. In this instance, I have always show thermal switches for the disconnecting means. Is that term still in use. When I do a google search for such a thing, I don't get anything actually called that. What SHOULD I be specifying. Note: It seems that conventional disconnect switches are limited to
 

masterinbama

Senior Member
Depends on if the motor is internally protected. If it is a 20 amp single pole with locking provisions is fine. If not a manua motor starter is required, in my opinion.

Sent from my LML211BL using Tapatalk
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
The term you probably are looking for is “manual motor starter”. Most of those fractional hp motors have built in OL protection though. You probably need to just spec a motor rated switch instead.
 