Yes.If it was wye & 240V, wouldn't the L-N voltage be 139V?
The source and usually the utility setvice drop that supplies the voltage is 3-phase 4-wire.I would call it "two out of three phase 120 wye". Often in apartment houses or other multiple occupancy situations the service is wye and each unit gets two out of three for 208/120 volts using a standard "single phase" panel. Which two are used is spread over the units in the building to best balance the phase loading.
Per IEEE, when the lower voltage is shown first, it is single phase and when the higher voltage is shown first it is 3 phase.For what it's worth I've heard some utilities call it Single Phase 120/208. As far as 'does it have a name' that's probably the best you can do.
Actually teaching the kids to understand it requires more than a name anyway.
What does multi-grounded neutrals have to do with the subject of this thread?This might help to explain.
What does multi-grounded neutrals have to do with the subject of this thread?
Still not sure what that has to do with a single vs 3 phase threadI thought it would help explain why there is current flow on the neutral when there is no load on the transformer.
Still not sure what that has to do with a single vs 3 phase thread
What problems are you talking about.When @Joethemechanic mentioned; Even if your 120 single phase loads are perfectly balanced you will have a neutral current. For me, it triggered my reference to current flow on the neutral(s) and my assertion that this is why there are so many problems with GFCI. And all neutral(s) in general. I guess, I am stuck on neutral !
What problems are you talking about.