Single-phase generator with 1.0 Power Factor

FaradayFF

Senior Member
Location
California
Hey guys,
For a single phase generator in the range of 22kW, with pf of 1.0, would we get 22kW only for purely resistive loads? The data sheet I'm looking at is confusing me, they are showing 22kVA and 27kVA for standby rating. Would we expect to get 27kVA out of this generator when it is powering inductive loads with 0.8pf?
Thank you,
EE
 
Top