I am working on designing a power distribution panel that will supply power to UV lamp ballasts. The power coming into the distribution panel is 240VAC 3-phase. Suppose I have three single-phase loads (where the load is an arrangement of ballasts), each 48 Amps. If the three loads are balanced (one load across phase a-b, one load across a-c, and one load across b-c), will the full-load amps of the power distribution panel be 48 Amps? In other words, will I need to size the main 3-pole circuit breaker for a 48 Amp load (of course I have to divide by 0.8 per NEC/UL, which would be 60 Amp)?
Upstream of the panel, there is a 480/240VAC 3-phase transformer. Not sure if it is delta or wye connected, or if it even makes a difference. Someone was telling me that I need to multiply the 48 Amps by the square root of 3 to get the FLA.
Does anyone have any answers or insight on the above? Any help would be very much appreciated. Thank you.