Hi Forum. I have a motor which the manual states is rated for 230V single phase, but the shop where I want to install has a panel with two hot leads, neutral, and ground. When I measure between each hot and neutral I see 125V. When I measure between hots I see 217V. So I need to describe this power to a technician who supports the product, a compressor. What is the proper way to describe this power ?
In describing it as two-phase, 217V, two legs of three phase, the technician says to try it, but I'm hesitant because my understanding of AC motors says you don't mix single and poly phase. If the motor nameplate specifies Voltage Range as 208-240 does it matter that in this case L1-L2 are not in phase ?
Sven
In describing it as two-phase, 217V, two legs of three phase, the technician says to try it, but I'm hesitant because my understanding of AC motors says you don't mix single and poly phase. If the motor nameplate specifies Voltage Range as 208-240 does it matter that in this case L1-L2 are not in phase ?