Strange question got asked of me today. I am bidding on a hanger that is being built on the back of a existing hanger. The back wall will be common to both buildings. Another electrical contractor told the owner a 3 phase builing could not connect or touch a single phase building. Is this correct can you give me a code refrence if it is?:confused: :confused:
 
Last edited:

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
The other EC is wrong. It is specifically allowed to have different systems serving buildings, see 230.2(D)

Roger
 

Gpelectrical

Member
Location
Canton,Ga
I thought that did not sound correct but wanted to have all my ducks in a row. Not to make the other guy look bad but give my customer the correct info. :grin:
 