Single phase to 3 phase converters

Status
Not open for further replies.

sparky 134

Senior Member
Location
Joliet, IL
Customer purchased a piece of 3 phase equipment and then realized he only has a single phase service so I'm looking for recommendations as to a manufacturer.
 
If it's motor driven, I know Teco makes some VFD's that'll take single phase at a 50% derate. Some Allen Bradley Powerflex's will do it also but only at 35% of normal 3 phase capacity.
 
Customer purchased a piece of 3 phase equipment and then realized he only has a single phase service so I'm looking for recommendations as to a manufacturer.

If it is simply a motor driven load it may be cheaper and easier to replace the motor.
 
Status
Not open for further replies.
Top