Such things exist or can be custom built; a quick google search for 'rotary converter' shows standard items up to 200 KW with larger sizes available on a custom basis.

But this begs the question: why? If you need that much power for a single load, then you can probably get 3 phase delivered for far less than the cost of the phase converter. If you have lots of smaller loads, then there are probably much better choices than a large single to three phase converter.

-Jon
 
winnie said:
But this begs the question: why? If you need that much power for a single load, then you can probably get 3 phase delivered for far less than the cost of the phase converter.
-Jon

Unless the OP is at the end of miles of a single phase line.:) In which case, you might check with the utility for load and voltage flicker if it is one big load.
 
Robz said:
Is their a converter that would go from 480 volt single phase to 480 volt three phase at 600 amp?
Holy dollars, Batman! That's a pretty special phase converter. Is utility 3-phase really that far out of the picture?
 