see 230.79(C) where it calls for 3-wire.:smile:Does the NEC allow (or prohibit) the use of a two wires (Phase + Neutral) service on a residential dwelling?
Thanks
Does the NEC allow (or prohibit) the use of a two wires (Phase + Neutral) service on a residential dwelling?
Thanks
230.79(C) only applies to SFDs. Also, there's a lot of 120v services still in use that were installed years ago.![]()