I have a customer that has a single phase, 10 kVA online UPS that is fed by a 60A 2P breaker in a 100A 3 phase 120/208 panel. The UPS feeds a single phase panel with 120 and 240 loads.
I want to calculate the actual load on the 3ph panel. Would my calculation be 1) 10kVA/(208*1.73) or 2) 10kVA/208?
Using method one I get 27.7A and method two 48A. Which is correct?
Thank you.
AF
I want to calculate the actual load on the 3ph panel. Would my calculation be 1) 10kVA/(208*1.73) or 2) 10kVA/208?
Using method one I get 27.7A and method two 48A. Which is correct?
Thank you.
AF