Single phase vs 3 phase systems
If you understand trigonometry and vector math, and apply it to three-phase and single-phase systems, it will be pretty obvious.
If you don't learn trigonometry and vector math, there is probably no approximate analogy that will make any sense. (with the possible exception of delta and wye diagrams carefully drawn to scale)
NEC itself doesn't require any particular color scheme for any voltage system. It does require identifying system and phase when there is more than one voltage system on the premises. There is widely used color schemes out there but are not a requirement unless you have local jurisdiction amendments that reference them.
If you only have one voltage system there is no requirement to identify phases other than high leg when you have such a system and the grounded conductor is also present at that location in the system.
As of 2020, which we’re on in California, orange is still required. “Or other effective means”, which I guess means you could hang a tag that says “High Leg”?
Ot was require for high leg, or something else?
Purple is required for the high leg.
Although I've seen orange in the city, too.
Actually if you keep reading you'll see they also mandate red and black for 120/240 and red black blue for 208/120.