Single Phase vs three phase

Status
Not open for further replies.

3nd4

New User
Location
HK
Hello,


I'm about to rent an industrial place and the real estate person tells me that a 100a three phase generator generators as many watts as 3 100a single phase generator. Is that correct?


I want to put computers there and need a lot of watts to power them if that helps.


Thanks a lot for your answers.
 
Generators are generally rated in watts, I’ve never seen one rated in amperes. Is this a hypothetical question, or does this machine exist?
 
no

assuming equal voltage

1 ph ~ 240 x 100 x 3 each = 72 kva
3 ph ~ sqrt3 x 240 x 100 x 1 each = 41.57 kva

this is hypothetical and the question is vague
3 gensets in parallel at this kva range is not good practice
 
Depends on the prime mover (engine) :D

All I can discern as a fact from the OP is that the real estate agent is either a liar or ignorant or both. :lol:

Or, maybe 120 X 100 X 3 = 36 ? vs 72 to make any kind of math comparison? assuming 3 separate loads .....

the OP snuck past the mods for all of 4 hours ?
 
Last edited:
Hello,


I'm about to rent an industrial place and the real estate person tells me that a 100a three phase generator generators as many watts as 3 100a single phase generator. Is that correct?


I want to put computers there and need a lot of watts to power them if that helps.


Thanks a lot for your answers.
They might want to stick with real estate, the answer isn't that simple.

If the rated current of both generators is 100 amps then the three phase unit will be capable of 1.73 times more watts then the single phase. The prime mover on the three phase unit will have more capacity also because it is capable of delivering more power.

Three 100 amp single phase generators would produce more power then a single 100 amp three phase unit.

All this is assuming same voltage rating on any of the units in question.

As mentioned not advisable to parallel this small of units. Also a single unit with needed capacity would likely be more efficient then three individual units regardless of whether it is single or three phase.
 
Three 100 amp single phase generators would produce more power then a single 100 amp three phase unit.

All this is assuming same voltage rating on any of the units in question.
That would seem to be an obvious take given that they are intended for the same facility.
The actual voltage doesn't matter. The kVA or VA will differ by the ratio √3.
 
That would seem to be an obvious take given that they are intended for the same facility.
The actual voltage doesn't matter. The kVA or VA will differ by the ratio √3.
I almost missed it myself but read OP carefully.

a 100a three phase generator generators as many watts as 3 100a single phase generator

3 100 amp single phase generators will be capable of more power then a single 100 amp three phase, won't be too significantly much more, and will very likely consume more fuel then a single unit with the same combined rating.
 
Sounds like your real-estate person has little or no expertise in electricity.

Is this industrial place powered by on-site generators or by a distribution line from a utility? If it doesn't use generators, the capabilities of generators is irrelevant.

Large motors (more than about 10 kilowatt) usually require a three-phase power supply and industrial buildings are usually supplied with three-phase power. Computers generally require only single phase. If the building is supplied with three-phase power, you can still power single-phase loads by simply not hooking up the other two phases. The only relevant question then becomes whether the incoming powerline can supply as much power (watts or VA) as your computers will consume.

Does "Location: HK" mean Hong Kong?
 
Hello,


I'm about to rent an industrial place and the real estate person tells me that a 100a three phase generator generators as many watts as 3 100a single phase generator. Is that correct?


I want to put computers there and need a lot of watts to power them if that helps.


Thanks a lot for your answers.

If the site is industrial why do you need generators?
 
curious

curious here also

First thought on reading OP was that there was going to be some operation in the rented location where power draw needed to be hidden from the authorities, such as pot growing in a local where it is illegal or bitcoin mining where regulated or taxed.
 
curious

curious here also

First thought on reading OP was that there was going to be some operation in the rented location where power draw needed to be hidden from the authorities, such as pot growing in a local where it is illegal or bitcoin mining where regulated or taxed.
Yeah, Hong Kong, I'm going to bet on Bitcoin mining...
 
no

assuming equal voltage

1 ph ~ 240 x 100 x 3 each = 72 kva
3 ph ~ sqrt3 x 240 x 100 x 1 each = 41.57 kva

this is hypothetical and the question is vague
3 gensets in parallel at this kva range is not good practice

Since we're talking hypothetical what if the OP is referring to 3-100 amp 120 volt generators versus a 3Ø, 100 amp, 208Y/120 volt generator?
 
Sounds like your real-estate person has little or no expertise in electricity.

Is this industrial place powered by on-site generators or by a distribution line from a utility? If it doesn't use generators, the capabilities of generators is irrelevant.

Large motors (more than about 10 kilowatt) usually require a three-phase power supply and industrial buildings are usually supplied with three-phase power. Computers generally require only single phase. If the building is supplied with three-phase power, you can still power single-phase loads by simply not hooking up the other two phases. The only relevant question then becomes whether the incoming powerline can supply as much power (watts or VA) as your computers will consume.

Does "Location: HK" mean Hong Kong?