LarryFine
Master Electrician Electric Contractor Richmond VA
- Location
- Henrico County, VA
- Occupation
- Electrical Contractor
It's my understanding that 220/240/250 volt services are supplied from wye systems.
But those voltages are the line to neutral voltage on those systems, there is no ~120 volt available.It's my understanding that 220/240/250 volt services are supplied from wye systems.
220V 50HzAs in 220/380 or 240/415 Wye?
Yes, but we don't have confirmation that it's actually in Hong Kong, and it doesn't change the answer.... but isn't hong kong's std 220 or 240?
Wherever you are, you can buy computers locally that are compatible with the local voltage. This would be an issue only if he were buying American or Canadian computers and installing them in Hong Kong. And maybe not even then because many computers are designed for 90-260 volts, 50-60 Hz.But those voltages are the line to neutral voltage on those systems, there is no ~120 volt available.
Yes, but we don't have confirmation that it's actually in Hong Kong, and it doesn't change the answer.
Single-phase loads can be powered from a three-phase supply, and only the capacity of the supply vs. the consumption of the load matters, not how it's configured.
Most residences here get single phase line to neutral that comes from a three phase source - the star secondary of a 3-phase distribution transformer.really? a single ph load can be supplied from a 3 ph source?:lol:
But those voltages are the line to neutral voltage on those systems, there is no ~120 volt available.
Most residences here get single phase line to neutral that comes from a three phase source - the star secondary of a 3-phase distribution transformer.
A few palatial mansions and high rise buildings have a three phase supply but domestic/residential equipment is single phase 230V.
I imagine it's similar in Hong Kong. I worked on some variable speed drives for cooling pumps there and the supply was 400V 3-phase just as it would be here.
ohmy what?uh uh !!??! hmy:
j/k
pretty sure I had heard somewhere the huge power grid generators are 3 ph
and almost all residential loads are served single ph
ohmy what?
I'm not sure what exactly you are questioning.
you guys are saying that from a 3 ph system a neut can be derived and one leg and the neut (ergo 1 ph) can serve a load and that is common practice!?!?? get the heck outta here!!
:roll:
I contend that if you tried such craziness that life as we know it will cease to exist and that time will reverse
this is known as the 'benjamin button' effect
Got in one!you guys are saying that from a 3 ph system a neut can be derived and one leg and the neut (ergo 1 ph) can serve a load and that is common practice!?!??
Gotta be true, I read about it on facebook. Honest injun!
whoa cowboy!! hold your horses and simmer down!!! you are talkin' loco bro' !!!
if what you guys say is true then if you equally load all 3 phases with identical 1 ph loads the neut current would be 0!!!!!
where does it go!!!!
where.....does.........it.............gooooooooooo!!!!!!!!
:lol:
Got in one!
A 400V star (wye) secondary on the distribution transformer gives 230V line to neutral. The star point.
Done here and elsewhere all the time.
I don't understand what difficulty you have with that.
if there is no current then your electric bill is zero, right?
It would sum to zero at the transformer star point, not the individual neutrals.whoa cowboy!! hold your horses and simmer down!!! you are talkin' loco bro' !!!
if what you guys say is true then if you equally load all 3 phases with identical 1 ph loads the neut current would be 0!!!!!
where does it go!!!!
where.....does.........it.............gooooooooooo!!!!!!!!
:lol:
It would sum to zero at the transformer star point, not the individual neutrals.