Single Pole Cam Lock Connectors Lockout

gfw5547

Member
Location
Salt Lake City
Occupation
Operation
Hi, I want to know if anyone with experience using the Cam Lock single pole connectors has any recommedations for lock out tag out methods?
I am looking for ways to lock the connectors when connected so no one inadvertantly opens the connector when energized.
I am looming to use Series 16/18 single pole cam lock connectors in 480V 250amp service (4/0 SOOW wire)
 
Hi, I want to know if anyone with experience using the Cam Lock single pole connectors has any recommedations for lock out tag out methods?
I am looking for ways to lock the connectors when connected so no one inadvertantly opens the connector when energized.
I am looming to use Series 16/18 single pole cam lock connectors in 480V 250amp service (4/0 SOOW wire)
Lock out tag out generally refers to ways to deenergize such things, not keep them energized.

My suggestion would be to get a junction box. Cut out the back and bottom. Mount the junction box over the connectors and run the cables out the bottom. Put a padlock on the junction box door.
 
I am looking for ways to lock the connectors when connected so no one inadvertantly opens the connector when energized.
Interesting question. We used Camloks all of the time for load bank testing but I never considered someone opening one while energized. I've never seen a commercial product that would lock these shut. I'm sure with some ingenuity you could make something that would serve this purpose.
 
@gfw5547 what's the application? Why would it need this protection? (Not saying there aren't places where it's a good idea, more that it's highly uncommon in my experience.)
We provide temporary water treatment solutions. We relocate every 2-4 months and one of our biggest mobilization costs is electrical, hard wiring and disconnecting every pump and mixer every move. I am thinking cam lock connectors make things a lot quicker but during operation I want to reduce the risk that someone will inadvertently open a medium voltage circuit during operation.
 
We provide temporary water treatment solutions. We relocate every 2-4 months and one of our biggest mobilization costs is electrical, hard wiring and disconnecting every pump and mixer every move. I am thinking cam lock connectors make things a lot quicker but during operation I want to reduce the risk that someone will inadvertently open a medium voltage circuit during operation.
Camloks are not rated for MV.
 
Ok, if you’re having that problem, then unqualified people are working in that area? Don’t know of anybody at a water treatment plant that wouldn’t get fired for disconnecting a piece of electrical equipment without authorization.
 