- Location
- Massachusetts
Smart $:
If there is already a GFCI upstream, single pole breaker instead of two pole breaker for an ungrounded 460V two wire system may be used. It results not only in safer operation but also may lower cost (single pole instead two pole breaker).
What do you think from the point of view of CMP?![]()
There is no such thing as a GFCI for 460 volts or for ungrounded systems.