What does the code say about when it is required to use a single receptacle vs. a duplex receptacle? I think a lot of times people install single outlets when they don't have to.
Thanks
Thanks
Ben Trueblood said:What does the code say about when it is required to use a single receptacle vs. a duplex receptacle? I think a lot of times people install single outlets when they don't have to.
Thanks
I believe that section applies if you use a single recep.lowryder88h said:The only one I can think of off the top of my (which at this time is pretty empty) NEC 210.21 (B)(1):-?
I guess I'm saying ,.. no , it does not have to be a single receptacle, whether it is on an individual branch circuit or not..:grin:wbalsam1 said:See 210.8(A) Exception #2. If only one cord-and-plug appliance, such as a refrigerator, freezer, table saw, or similar item, were to occupy that dedicated space, then a single receptacle would be required.
wbalsam1 said:For example: a single receptacle on an individual circuit must have an ampere rating as per Table 210.21(B)(3).
pete m. said:I guess what I'm asking is; If a duplex receptacle is installed in the middle of the wall space in a garage and the electrician marks the top half for a freezer and the bottom half for a refridgerator does this meet the intent of the aformentioned exception (dedicated space) if the appliances are not installed at the time of inspection?
Pete
wbalsam1 said:Hi: ... So the "dedicated space" is really only for 1/2 of the duplex. In this example I would require a single receptacle for the appliance, or leave the duplex and GFCI protect it.