#1. When sizing the GEC for a separately derived system the GEC is sized in accordance with the primary conductors that supply the feed to the transformer. Correct? Based on table 250.66.
#2 Primary Conductor OCP on say for instance 30 kva transformer @ 480volt primary. Conductor OCP is 125% FLC.
As in 36.1 *125%= OCP
Primary conductors sized in accordance with this calulation.
I guess this really three part question.
#1. When sizing the GEC for a separately derived system the GEC is sized in accordance with the primary conductors that supply the feed to the transformer. Correct? Based on table 250.66.
#2 Primary Conductor OCP on say for instance 30 kva transformer @ 480volt primary. Conductor OCP is 125% FLC.
As in 36.1 *125%= OCP
Primary conductors sized in accordance with this calulation.
I guess this really three part question.