More out of curiosity then anything else, but how does a single solenoid ATS achieve two switching directions? This has me really intrigued.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I'm pretty sure that they use DC solenoids with a rectifier. Could be they reverse polarity.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
I'm pretty sure that they use DC solenoids with a rectifier. Could be they reverse polarity.

Most do, but the switching is done at the AC side. One pulse to switch to emergency, one pulse latter for normal. Though I could be wrong on how it happens.
 

kwired

Electron manager
Location
NE Nebraska
Most do, but the switching is done at the AC side. One pulse to switch to emergency, one pulse latter for normal. Though I could be wrong on how it happens.
Sounds more like an impulse relay (alternating relay) - every time it gets signal to coil it reverses output contact connection. Would need to have some extra logic to determine which state it is in so it doesn't send a signal to the coil to transfer when there is no need to.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Sounds more like an impulse relay (alternating relay) - every time it gets signal to coil it reverses output contact connection. Would need to have some extra logic to determine which state it is in so it doesn't send a signal to the coil to transfer when there is no need to.

It has the logic- when the ATS transfers to normal it breaker the normal "call", when transferring to emergency it breaks the emergency "call", both done via microswitch.
 

ATSman

ATSman
Location
San Francisco Bay Area
Occupation
Electrical Engineer/ Electrical Testing & Controls
When I think of a single solenoid ATS, GE-Zenith and ASCO come to mind. They both use a single Solenoid with one coil that is fed from a bridge rectifier. It uses an over-toggle cam type of mechanism that switches direction of the main contact closure. On the first pulse from the controller the solenoid plunger pulls in and rotates the cam in the clockwise direction to close contacts to emergency. On the second pulse the plunger pulls in and rotates the cam in the counter-clockwise direction. There is no change in polarity of the voltage to the coil (see attached dwg) The over-toggle action of the cam mechanism is what determines which set of contacts close.

With the GE-Z units this type of design is usually seen on the smaller switches (60-400A)
Two solenoids are used on larger units that pull in to close in to each source.
On the ASCOs the larger units use a single solenoid with (2) coils that are wound opposite to change
direction of the plunger and contact mechanism.
With all ATS manufactures, the standard design is after the unit switches sources, voltage is removed and the contacts are mechanically held closed.
 

Attachments

  • GE 70A-1000 ZTG 225A_18002.pdf
    80.6 KB · Views: 6

mbrooke

Batteries Included
Location
United States
Occupation
Technician
When I think of a single solenoid ATS, GE-Zenith and ASCO come to mind. They both use a single Solenoid with one coil that is fed from a bridge rectifier. It uses an over-toggle cam type of mechanism that switches direction of the main contact closure. On the first pulse from the controller the solenoid plunger pulls in and rotates the cam in the clockwise direction to close contacts to emergency. On the second pulse the plunger pulls in and rotates the cam in the counter-clockwise direction. There is no change in polarity of the voltage to the coil (see attached dwg) The over-toggle action of the cam mechanism is what determines which set of contacts close.

With the GE-Z units this type of design is usually seen on the smaller switches (60-400A)
Two solenoids are used on larger units that pull in to close in to each source.
On the ASCOs the larger units use a single solenoid with (2) coils that are wound opposite to change
direction of the plunger and contact mechanism.
With all ATS manufactures, the standard design is after the unit switches sources, voltage is removed and the contacts are mechanically held closed.

Yup- this is an ASCO ATS.

I have to admit that the concept is genius. Never thought you could do it, but they did. Kudos to smart inventing!
 

kwired

Electron manager
Location
NE Nebraska
When I think of a single solenoid ATS, GE-Zenith and ASCO come to mind. They both use a single Solenoid with one coil that is fed from a bridge rectifier. It uses an over-toggle cam type of mechanism that switches direction of the main contact closure. On the first pulse from the controller the solenoid plunger pulls in and rotates the cam in the clockwise direction to close contacts to emergency. On the second pulse the plunger pulls in and rotates the cam in the counter-clockwise direction. There is no change in polarity of the voltage to the coil (see attached dwg) The over-toggle action of the cam mechanism is what determines which set of contacts close.
Exactly what I was trying to describe before - there are "alternating relays" and some of the old "touch plate" low voltage lighting relays used similar concept - every time you energize the coil the output changes to opposite state.

Most "alternating relays" used for things like dual pump stations use an electronic or combination of electronic and mechanical to get the job done, but a purely mechanical alternating relay is exactly what is being described here, it's output contacts change state every time the coil is actuated.
 

ATSman

ATSman
Location
San Francisco Bay Area
Occupation
Electrical Engineer/ Electrical Testing & Controls
Exactly what I was trying to describe before - there are "alternating relays" and some of the old "touch plate" low voltage lighting relays used similar concept - every time you energize the coil the output changes to opposite state.

Most "alternating relays" used for things like dual pump stations use an electronic or combination of electronic and mechanical to get the job done, but a purely mechanical alternating relay is exactly what is being described here, it's output contacts change state every time the coil is actuated.

Kwired, I'm very familiar with an alternating relay for equalizing the run times on a dual pump setup and this is not that.
This mechanism is part of the ATS main contact assembly and has no electrical contacts.
Next time you're near a small ATS take a look at the solenoid and the mechanism connected to the plunger to see what I'm trying to describe. If I find a pic I will post it.
 

kwired

Electron manager
Location
NE Nebraska
Kwired, I'm very familiar with an alternating relay for equalizing the run times on a dual pump setup and this is not that.
This mechanism is part of the ATS main contact assembly and has no electrical contacts.
Next time you're near a small ATS take a look at the solenoid and the mechanism connected to the plunger to see what I'm trying to describe. If I find a pic I will post it.
Modern alternating relays for pump stations are not what I am talking about. Those usually are solid state driven even if there is electromechanical components. You lose main power to the solid state component and you may "alternate" the output when power comes back. I recently purchased one that is purely electromechanical, (I believe it was a Tyco/P&B product) and had somewhat at hard time finding what I was looking for. It likely is similar mechanical concept to the ATS solenoids OP is talking about, just smaller in size. Only two coil leads, every time the solenoid operates the mechanism attached alternates which way the double throw switch it drives makes connection.

I was using it for reversing direction of a machine, both with automatic controls when a physical barrier was reached as well as with a manual pushbutton to change direction on demand. We didn't want it to reverse when utility power was lost (which it regularly can be because of load management controller) and then restored again. I wanted to use other types of alternating relays but that was not acceptable for it to change state when power was lost then restored again. All the ones that were readily available and at least partly solid state driven always went back to output 1 after a power loss. This one only changes state whenever the solenoid is actuated.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Kwired, I'm very familiar with an alternating relay for equalizing the run times on a dual pump setup and this is not that.
This mechanism is part of the ATS main contact assembly and has no electrical contacts.
Next time you're near a small ATS take a look at the solenoid and the mechanism connected to the plunger to see what I'm trying to describe. If I find a pic I will post it.



Dislike having to use this one, but here is a schematic to an old late 60s single solenoid dual ATS. "TS" is the transfer mechanism actuating solenoid, LO (and LOE) is a voltage/frequency relay which closes upon the correct thresholds being reached. 1V,2V and 3V are under voltage relays that drop out on low voltage and close at nominal voltage. The rest I think is self explanatory.
 

Attachments

  • Old ATS.jpg
    Old ATS.jpg
    137.3 KB · Views: 1