mivey said:You might consider that GE has no problem with the term 120/208 single phase:
I agree. "serve single-phase loads" vs "single-phase service" just doesn't seem like it is worth the time. There has to be something more entertaining to do.hardworkingstiff said:Mivey,
I know this is nit picking, but they did not call it a single-phase service, just that single-phase loads could be served.
I'll let it go, because I guess it really doesn't matter.
POWER_PIG said:It's all very simple......and it's prob. been stated here in previous post, but forgive me for not going back in time to see. It's called single phase because there is only one phase. (pretty simple eh?) calling L1 and L2 "A" phase and "B" phase is where the confusion sets in. In a single phase installation there is only one secondary phase in relation to the primary. In a 120/240 install, you will have only one 240 volt " phase." Now bring out the center tap and now you have two half phases.....generally called line 1 and line 2 and they will read 120 line to neutral (center tap).
It's called 3 phase when you have 3 single phase pots (windings) wired in series or in parrallel depending on the config. A "wye " is 3 windings wired in parallel, and a "delta" is 3 pots (windings)wired in series. thats the just of it, until you get into 2 pot banks like an open delta secondary/open wye primary.
I already understand the concept thank you,,,,just trying to give a much simpler explanation, thats all.hardworkingstiff said:See posts 36 & 37 in this thread.
Yes - What do you want looked up?mivey said:Does anybody have the IEEE dictionary? ...
Could be. Maybe I'm letting the neutral confuse the issue. Maybe it is 120 volt single phase loads (L1-N), then 208 single phase loads (L1-L2) separately and quit worrying about the L1-N-L2 path.POWER_PIG said:Only using, say L1 and L2 of a 120/208 volt 3 pot bank to serve single phase loads, would it not be accurate to say that L1 and L2 now become 2 windings wired in series forming one 208 volt phase?........maybe?
It does seem to say single phase is zero or 180 degrees difference. It is just hard to tear away from being able to take a single phase load and hook it up to a single phase 120/240, then be able to take the same single-phase load and hook it up to three phase or I guess it is actually 2 of 3 phases. I do like the sound of "2 of 3 phases".hardworkingstiff said:I believe the 120/208 (2 of 3 phases) does not meet the IEEE definitions of single-phase that Mivey posted.
I think it's just 2 of 3 phases, and not single-phase.
mivey said:What do they call a 3-wire 120/208 service: single-phase, three-phase, portion-of-three phase, etc....
Probably more efficient than a 90* 2phase. And if you looked at the waveforms of A/N and B/N you would have two distinctive waveforms clearly out of phase with each other. Oh I think I gotta go now I have said enough.crossman said:We could build a 120/208 squirrel cage motor which used two of the phase conductors and the neutral. The stator would certainly create a rotating field much like that of the three phase squirrel cage motor stator. There would be no need of starting capacitors or shaded poles or start windings or any of that stuff like is required with single phase systems. So my thought is that 120/208 with two phase conductors and the neutral is not a single phase system.
Rick Christopherson said:I can't believe I didn't see this thread until today. :grin: Jeeze, I am bored.
How the heck can anyone justify calling a 120/208 system as single phase? It would be OK calling L1-L2/208 a single phase source, but as soon as you add the 120/208, this is no longer an option.
In reading this thread, I think it helped solidify my original thought that the 3-wire 120/208 is single phase. There were many good posts but I saved #54, #61, and #66 for future reference.winnie said:This exact point gets debated over and over and over. See for example: