charlie b said:I suppose that once you get over a couple hundred miles or so away, voltage drop might start becoming an issue.:grin: But the NEC does not have a limit for the distance between a motor and its controller.
Both the motor and the controller need to have a disconnecting means, and it has to be within sight (i.e., 50 feet maximum) of the device that it disconnects. But they don't have to be close to each other.
Both the motor and the controller need to have a disconnecting means, and it has to be within sight (i.e., 50 feet maximum) of the device that it disconnects. But they don't have to be close to each other.
augie47 said:charlie ???
Perhaps I should have begun with "The motor and the controller each need," instead of "both . . . need." It might have made my meaning clearer.charlie b said:Both the motor and the controller need . . . and it has to be within sight . . . of the device that it disconnects.
charlie b said:Was my wording not clear? Let me try again.
(1) The controller needs a disconnecting means. It must be within sight of the controller. 430.102(A).
(2) The motor needs a disconnecting means. It must be within sight of the motor. 430.102(B).
(3) Item #1 need not be close to Item #2.
Did I get some part of that wrong? It's not impossible, as motors are not my best friends, and 430 is not my favorite bedtime story.![]()
Perhaps I should have begun with "The motor and the controller each need," instead of "both . . . need." It might have made my meaning clearer.
True, there are two exceptions that allow a remote (locable) disconnect, but I don't encounter them often myself.augie47 said:Not "wrong" per se, but, per 430.102(B) I believe as long as the disconnect means is individually lockable, it does not have to be "in sight of the motor"..
In that case, now returning the original question, that disconnect would have to be in sight (50 feet max) of the motor.augie47 said:It is fairly commonplace in these parts to have a lockable disconnect at the controlller..which satisfies the motor disconnect rule.
Gus,augie47 said:Not "wrong" per se, but, per 430.102(B) I believe as long as the disconnect means is individually lockable, it does not have to be "in sight of the motor"..
It is fairly commonplace in these parts to have a lockable disconnect at the controlller..which satisfies the motor disconnect rule.