Originally posted by iwire:
I am still wondering why Ronald thinks he is not liked here? :confused:
Me too. :confused:

Roger
 
Re: Site Ltg Non-upsized equipment ground

Ronald I have lost a few myself :eek: But I think it was because I posted in a thread that was double posted and the one I posted to went off the radar screen. Now I have a icon to my post that will take me to all of my post and one that takes me to most recent posts.
 
Re: Site Ltg Non-upsized equipment ground

Originally posted by iwire:
I do not think it would make much difference if it is a 20 or 60 amp breaker.
That sounds reasonable. But then why do we even need a larger EGC for a 100A breaker? It has to be because we have larger phase conductors for a 100A circuit. So I really should have said "A number 10 is good for phase conductors up to a #6".

I think the real issue here is that the NEC wants the EGC sized based on the size of the phase conductors. So why don't they just get rid of table 250-122, and replace it with a table that relates the EGC size to the phase conductor size?

STeve
 
Re: Site Ltg Non-upsized equipment ground

Caution must be observed in increasing the circuit Overcurrent device from 20 amperes to 40amps where the lampholders at the pole lighting fixture are not of the heavy-duty type. See section 210.23(C).
 
Re: Site Ltg Non-upsized equipment ground

Originally posted by john m. caloggero:
Caution must be observed in increasing the circuit Overcurrent device from 20 amperes to 40amps where the lampholders at the pole lighting fixture are not of the heavy-duty type. See section 210.23(C).
Does this section apply even if there were inline fuses at the base of each pole that protected the luminaire at 15 amps or less?
 