How so?
In the ones I have seen, the generator output goes directly into the transfer panel rather than looping through the main panel. That makes all of the transfer panel to main panel wires one way with no balancing current when operated off the generator.
If the total feed from both generator phases happens to match, then there will still be no net current in the raceway. But if you turn on (transfer) only one branch you have 100% imbalance.
I probably should have said "is not guaranteed to be balanced."
A switch leg is always exactly balanced to zero net current, without involving the neutral.