don't cut yourself short, you were doing a fine job, you do Foghorn Leghorn as well as I did.it's hard to carry on a conversation with a chicken.
No this is a 400 amp panel with breakers in it that total 500 amps.Originally posted by volt101:
OK Lets do the math
Since you stated that you put non-reversing screws in the bus, I am GUESSING that this panel does not have a main. Now lets do the math..
2-150/3 = 300a 300a 300a
1-100/3 = 100a 100a 100a
1-100/2 = 100a 100a 000a
---------------------------
500a 500a 400a
This was a 400 amp panel with 500 amps on it?
That being the case 230.90(A)Exception No. 3 would allow the the OCP to exceed the panel rating.Service Conductors. The conductors from the service point to the service disconnecting means.
This how I see it I am intrested in how others see it.230.90(A)Exception No. 3: Two to six circuit breakers or sets of fuses shall be permitted as the overcurrent device to provide the overload protection. The sum of the ratings of the circuit breakers or fuses shall be permitted to exceed the ampacity of the service conductors, provided the calculated load does not exceed the ampacity of the service conductors.
Am I missing something because I think this is making Iwire's point?Nothing to do with loads. Just simple math.
What I am trying to express is
408.16 B Exception
230.71
230.90 A Exception 3
this would not apply to the issue in this thread.In addition to the requirements of 408.13, a power panelboard with supply conductors that include a neutral and having more than 10 percent of its overcurrent devices protecting branch circuits rated 30 amperes or less shall be protected by an overcurrent protective device having a rating not greater than that of the panelboard .