I was curious to know why I was seeing some of the responses I saw so I just went back and re-read the OP. It looks like I need to go back to school and take some reading lessons. The Op stated the following :If it's a main lug panelboard wouldn't there be a feeder disconnect for that panelboard at the main breaker panel ? In that case I don't see how or why the six switch rule would even apply.
I'll take that recipe for crow now.![]()
A disconnect at another building would not satisfy code at a separate structure. The disconnect must be at the separate structure, IMO.
225.32 Location. The disconnecting means shall be installed
either inside or outside of the building or structure
served or where the conductors pass through the building or
structure. The disconnecting means shall be at a readily
accessible location nearest the point of entrance of the conductors.
For the purposes of this section, the requirements
in 230.6 shall be utilized.