kennyp
Member
- Location
- Charleston, SC
I have a problem with a feeder size to a 277/480 to 120/208 step down xfmr. The xfmr is a 75kva left in the existing space by the old tennant and the new one wants to use it to feed a 100 amp 3 phase panel. The new service is 350 feet from where I want to install the xfmr and panel. All the voltage drop calculators I go to calculate a #1 thhn be used for not more than a 3% voltage drop. The contractor has an engineer that says I can feed it with a #4. I don't feel comfy with that. 
I am using a 60 amp cont. and 40 non cont. load for the calc.
I am using a 60 amp cont. and 40 non cont. load for the calc.