We have a ground ring at the generators and another one at the building sized the same. Question is what size the bonding jumper needs to be.
I think it is pretty straightforward. 250.53(C) tells you to size the grounding electrode per 250.66. It is a 2000A 480V service with largest ungrounded conductors being (8) sets of #350 AL. Equivalent area is 8x350=2800 kcmil. Our grounding electrodes are copper, so 3/0 is required - correct?
Unfortunately 2/0 was specified and is already installed, the trenches have all been backfilled. So a new trench would be required to get a 3/0 installed. I am a very by-the-book engineer but wonder if this something worth approaching the electrical inspector about. I know enough about grounding to know what is code, but not enough to make a judgment call as to whether the system is intrinsically safe as it is currently installed. Any thoughts on this? I don't want to propose something to the inspector that is a bad idea.
For what it's worth, the owner only cares that the system meets Motorola R56. We started with a 4/0 but as part of VE this was reduced to a 2/0, which still met R56...but no one bothered to check and see that it still met NEC.
Thanks!
We have a ground ring at the generators and another one at the building sized the same. Question is what size the bonding jumper needs to be.
I think it is pretty straightforward. 250.53(C) tells you to size the grounding electrode per 250.66. It is a 2000A 480V service with largest ungrounded conductors being (8) sets of #350 AL. Equivalent area is 8x350=2800 kcmil. Our grounding electrodes are copper, so 3/0 is required - correct?
Unfortunately 2/0 was specified and is already installed, the trenches have all been backfilled. So a new trench would be required to get a 3/0 installed. I am a very by-the-book engineer but wonder if this something worth approaching the electrical inspector about. I know enough about grounding to know what is code, but not enough to make a judgment call as to whether the system is intrinsically safe as it is currently installed. Any thoughts on this? I don't want to propose something to the inspector that is a bad idea.
For what it's worth, the owner only cares that the system meets Motorola R56. We started with a 4/0 but as part of VE this was reduced to a 2/0, which still met R56...but no one bothered to check and see that it still met NEC.
Thanks!