Both.What I meant is what are terminals considered in a panel? The main lugs, the breakers????
Both.What I meant is what are terminals considered in a panel? The main lugs, the breakers????
So a panel with have the terminal temperature ratings for both the mains and the branch?Both.
So a panel with have the terminal temperature ratings for both the mains and the branch?
Don's post seemed to indicate the opposite which kind of confused me.Definitely the mains, if it's main lug.
Ungrounded branch conductors would land on the breakers and be determined by the breaker lug ratings. But neutral conductors would land on the panel neutral bar and be determined by the neutral bar temp rating. I suppose the label could be justified for the neutral bar they provided. Very unusual though.
I can definitely see the ratings applying to the connections that are part of the panel but do the panels limits also apply to the third party circuit breakers?It is my opinion, that the 60°C ampacity limit in the picture that was posted only applies to conductors that are connected to a circuit breaker terminal.
Like, I said, a terminal is any thing that you connect a wire to any where in the equipment.I should have clarified sorry. I know exactly what terminals are. What I meant is what are terminals considered in a panel? The main lugs, the breakers????
I stand by my statement that the note calling for a 60°C ampacity on that equipment only applies to conductors connected to circuit breakers. There will be ratings for the other terminations, but I do not see that note as applying to other terminations.Don's post seemed to indicate the opposite which kind of confused me.
I can definitely see the ratings applying to the connections that are part of the panel but do the panels limits also apply to the third party circuit breakers?
How would it not apply to the neutral bar terminations?I stand by my statement that the note calling for a 60°C ampacity on that equipment only applies to conductors connected to circuit breakers. There will be ratings for the other terminations, but I do not see that note as applying to other terminations.
It might, but there would be no reason for it to apply to anything other than the breaker terminals and that is how I would read it.How would it not apply to the neutral bar terminations?
Where else would other termination ratings be labeled?