davedottcom
Senior Member
Building my 1st 400 Amp service tomorrow!
here's my set up:
400 A Milbank Meter / underground fed
3 Double Lugs on secondary side
Using 4/0 AL to (2) 200 Amp Main Breaker panels
2 seperate 2" pvc pipes, 2 seperate feeds,
(no parallel feeds, no tapping.)
# ? GEC from meter can to grounding electrodes
I'm looking at Table 250.66 and according to the chart a #4 solid copper is acceptable for the 4/0 AL Service Entrance Conductor. But, now the Fine Note #1 below the chart is confusing me.
Notes:
1. Where multiple sets of service-entrance conductors are used as permitted in 230.40, Exception No.2, the equivilent size of the largest service-entrance conductor shall be determined by the largest sum of the areas of the corresponding conductors of each set.
230.40 Exception 2 is basically saying that "Tapping" is permitted, Right?
This should have no bearing on my "set up" since I'm not tapping.
I've read it ten times and I can't make sense out of the 250.66 Note #1!
Dave
here's my set up:
400 A Milbank Meter / underground fed
3 Double Lugs on secondary side
Using 4/0 AL to (2) 200 Amp Main Breaker panels
2 seperate 2" pvc pipes, 2 seperate feeds,
(no parallel feeds, no tapping.)
# ? GEC from meter can to grounding electrodes
I'm looking at Table 250.66 and according to the chart a #4 solid copper is acceptable for the 4/0 AL Service Entrance Conductor. But, now the Fine Note #1 below the chart is confusing me.
Notes:
1. Where multiple sets of service-entrance conductors are used as permitted in 230.40, Exception No.2, the equivilent size of the largest service-entrance conductor shall be determined by the largest sum of the areas of the corresponding conductors of each set.
230.40 Exception 2 is basically saying that "Tapping" is permitted, Right?
This should have no bearing on my "set up" since I'm not tapping.
I've read it ten times and I can't make sense out of the 250.66 Note #1!
Dave