Hi
I have a question on sizing a EGC for a parallel feeder. It is for a solar field 900' away from the buildings service. Its full loads current is 800A and the OCPD is set at 1000A without GFP. (I don't think I need GFP because solar in not considered a service)
I am using 6-sets (3-600AL, 1-3/OAL N and 1-?AL G)
According to 250.122 the EGC for 1000A would be 4/O AL
The increased size for voltage drop is 2/O to 600 for the 133A feeders
250.122(B) requires the EGC be increased proportionally to the ungrounded conductors.
The 600 is 4.5 times larger than the 2/O per CM
so I would need a min of 4.5*211,592(the CM of 4/O) = 954,033CM.
250.122(F) requires a full EGC per set.
Does this mean I need to add (2) 500kcml AL conductors to each set for the EGC or can it be reduced to (1) 600kcml AL to match the largest ungrounded conductor in the set per 250.122(A)?
Is there an exception when using an OCPD with GFP?
I found one for cables but it does not seem to fit here.
Also if there is an exception, I would probibly need GFP on the OCPD coming from the solar field also?
Seems unnecessary for the ground to be larger then the feeder.
Thanks
Thanks