sticko
Member
- Location
- nothern virginia
They are pulling (20) 10-4 MC cables to a 24 X 24 pullbox, then by using (2) FMC nipples to a PDU. The grounding conductors are terminated in an added ground bar in the pull box. The plan was to pull one #10 grounding conductor in each of the FMC nipples to the ground bar in the PDU. The main breaker in the PDU is rated at 225 amps. The MC cables are rated at 20 amps each. I thought the grounding conductor needed to be sized per NEC 250-122. For a 225 amp OC device, a #4 AWG grounding conductor was needed. Can you tell me if I'm wrong? All 20 MC cables terminate in the pull box, under the floor and the grounded and ungrounded conductors are routed through the nipples to the PDU. I hope I am clear with my description. Thanks.