Power Distribution Unit?
Sent from my Droid Maxx
Sent from my Droid Maxx
If you add an additional 100 amp circuit to the pull box later you will pull a correctly size EGC with the new 100 amp conductors. I don't see any reason to increase the EGC for circuits that don't exist.
I have always been taught that you can derate the EGC 1 size. But I have never seen where in the code it states that it is ok.
But every electrician I have worked with does it. So in the OP's case, you could run a #12 ground?
I see that a #10 ECG is good for up to 60A. At least that's what I got from looking around. 250.122 2008 is what I was looking at.
So now I'm a bit cornfused. Because you can't run 10awg conductors for a 60 amp circuit. Am I looking at the wrong info?
I see that a #10 ECG is good for up to 60A. At least that's what I got from looking around. 250.122 2008 is what I was looking at.
So now I'm a bit cornfused. Because you can't run 10awg conductors for a 60 amp circuit. Am I looking at the wrong info?
Additional sales of copperand what would you gain if you did?