Table 250.66 shows the minimum size of GEC, but, what if the service entrance conductors is sized lower than #8 AWG, would i still used the minimum #8 AWG for GEC?
how about the grounded service conductor? 250.24 (C) (1) says that the grounded service conductor shall not be smaller than the required electrode conductor specified in table 250.66 but shall not be required to be larger than the largest ungrounded service entrance phase conductor.