peter d
Senior Member
- Location
- New England
No "oops" there because generally the conductors on the load side of the meter are the larger conductors. :smile:
That is true. I think it's a rare case when/if they will exceed the line side conductors.
No "oops" there because generally the conductors on the load side of the meter are the larger conductors. :smile:
Note 1 of T.250.66 requires the combined size of the two 4/0s.
I will go on to point out in this particular case the 350s do not exist to the NEC.
Agreed. I was getting hung up on what Pierre had said in post #4 about running one conductor back and sizing it as such. Since the conductors feeding the meter are not service entrance conductors (in this case) then they're irrelevant.
That is true. I think it's a rare case when/if they will exceed the line side conductors.
thanks gentleman for a great discussion on this thread.
I think i found my ans. Note 1 table 250.66 Also Exhibit 250.28 Pg. 214 of the NECH shows a example.
In almost any multiple service disconnect installation the combined total size of the smaller conductors will be larger then the large conductors. I also suggest that you forget about the 'line side' 'load side' and the meter(s) (Did that make sense)
The grounding electrode is a metal water pipe in the original post...so this would be required to be bonded with a #2 copper conductor per 250 104(A)(1)[/QUOT
If #2 aluminum is used for Bobs 6 meter service it would also require #2 copper.( I think )
Doesn't this contradict 310.15(B)(6)?Service conductors supplying a single service disconnect are required to have an ampacity at least as high as the overcurrent device. See 230.90(A) {You could actually apply the rules of 240.4(B) as well, see 230.90(A) Exception 2}
Service conductors supplying multiple service disconnects are required to have an ampacity only as high as the calculated load. See 230.90(A) Exception 3.