Good day just want to ask about the size of conductor you would recommend for use in a 2000A 3 phase main feeder for a residential building?
Good day just want to ask about the size of conductor you would recommend for use in a 2000A 3 phase main feeder for a residential building?
Good day just want to ask about the size of conductor you would recommend for use in a 2000A 3 phase main feeder for a residential building?
14 sets of 1/0.
6 sets of 500 CU assuming 4CCC = 2064A
or
8 sets of 300 CU assuming 4CCC = 2048A
Why 4 CCC's?
310.15(B)(5)(c). Based on the posed question, we either need to assume a majority of the load is nonlinear OR we need to assume it is not. I am making the assumption it is to be on the safer side.
OP said residential. Doubtful that the majority of loads is non-linear.
computers, cell and tablet charges, microwaves, possibly LED lighting, flat screen TVs, newer refrigerator, the list goes on. What would be non-linear; no current returning on the neutral? Since we do not know for fact, it is an assumption either way would it not be?
What would be non-linear; no current returning on the neutral?
computers, cell and tablet charges, microwaves, possibly LED lighting, flat screen TVs, newer refrigerator, the list goes on. What would be non-linear; no current returning on the neutral? Since we do not know for fact, it is an assumption either way would it not be?
If you are looking for a rule you can blindly apply, I have nothing for you.Non-linear loads put harmonic currents on the supply circuit. In particular, it is the 3rd harmonic and other multiples of 3, that matter most. 180 Hz when 60 Hz is the nominal frequency, and multiples thereof.
Unlike the fundamental 60 Hz currents that add up to zero when loads are balanced, 3rd harmonic currents and subsequent multiples accumulate constructively on the neutral, even if the three phases are balanced. So when these harmonic currents are significant, the neutral carries enough current to generate heat, even with balanced phase conductors.
Can anyone speak to how you would quantify the 50% nonlinearity of a mix of loads? In otherwords, what would I look for on a datasheet, and how would I add up the value for all loads in a given panelboard?
What would be non-linear; no current returning on the neutral? Since we do not know for fact, it is an assumption either way would it not be?
Given modern energy and interference requirements for lights, for TVs, and for computer power supplies, I would have to say very little.Just to clarify this, I understand what non-linear loads are. I was asking what loads would one assume for a residential project would not be considered non-linear?
99% of what I get involved with is industrial now, but I just did some volunteer work at an applicable project this week. It's a managed care facility, mostly developmentally disabled people so the 18 individual living units do not have stoves or ovens. The heat and water heater system is all gas and the commercial kitchen is all gas cooking. The electric loads are the elevator, which has a VFD on it (I was the one to discover that so I know for sure), the 2 Air Handlers, which is where they are wanting to ADD new VFDs, and the plugs and lights. All of the 18 rooms have TVs plus a giant screen system in the entertainment room, they estimated that almost all of the residents have some sort of gaming system hooked up to the TVs and some sort of music system, most of them have PCs or tablets, and all of the lighting is either Fluorescent, CFL or LED. The only significant electrical loads I found that were linear were the 2 large commercial refrigerators and a freezer (the laundry is off site). My estimate was 90% non-linear loads! It was kind of an eye opener really.A good portion of the load in a residential building is 3Ø elevators, fans, pumps, heaters, etc. IMO there are no real sizable harmonic loads that would get you near the 50% threshold.
99% of what I get involved with is industrial now, but I just did some volunteer work at an applicable project this week. It's a managed care facility, mostly developmentally disabled people so the 18 individual living units do not have stoves or ovens. The heat and water heater system is all gas and the commercial kitchen is all gas cooking. The electric loads are the elevator, which has a VFD on it (I was the one to discover that so I know for sure), the 2 Air Handlers, which is where they are wanting to ADD new VFDs, and the plugs and lights. All of the 18 rooms have TVs plus a giant screen system in the entertainment room, they estimated that almost all of the residents have some sort of gaming system hooked up to the TVs and some sort of music system, most of them have PCs or tablets, and all of the lighting is either Fluorescent, CFL or LED. The only significant electrical loads I found that were linear were the 2 large commercial refrigerators and a freezer (the laundry is off site). My estimate was 90% non-linear loads! It was kind of an eye opener really.