Good day just want to ask about the size of conductor you would recommend for use in a 2000A 3 phase main feeder for a residential building?


Hard to give a definitive answer without more information. Are these service conductors or a feeder? What type of equipment do they terminate on? Are you familiar with table 310.15(b)(16) and which temperature column to use?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Good day just want to ask about the size of conductor you would recommend for use in a 2000A 3 phase main feeder for a residential building?


There are many variables but for us we would likely use 5 sets of 600 kcmil copper conductors. 420*5=2100 amps
 

rojhan123

Member
Location
Philippines
I mean sir service conductor..,yup i'm familiar with that, so i am asking now is what size of parallel set of conductors would be recommended to be used for that 2000AT main breaker?
 

mjmike

Senior Member
OP said residential. Doubtful that the majority of loads is non-linear.

computers, cell and tablet charges, microwaves, possibly LED lighting, flat screen TVs, newer refrigerator, the list goes on. What would be non-linear; no current returning on the neutral? Since we do not know for fact, it is an assumption either way would it not be?
 

jumper

Senior Member
computers, cell and tablet charges, microwaves, possibly LED lighting, flat screen TVs, newer refrigerator, the list goes on. What would be non-linear; no current returning on the neutral? Since we do not know for fact, it is an assumption either way would it not be?

Yep, but I have not seen any real studies or info that says a standard resi noodle is likely to be a CCC.

What would be non-linear; no current returning on the neutral?

Nonlinear Load.
A load where the wave shape of the
steady-state current does not follow the wave shape of the
applied voltage.

Informational Note: Electronic equipment, electronic/
electric-discharge lighting, adjustable-speed drive sys-
tems, and similar equipment may be nonlinear loads
 

Carultch

Senior Member
Location
Massachusetts
computers, cell and tablet charges, microwaves, possibly LED lighting, flat screen TVs, newer refrigerator, the list goes on. What would be non-linear; no current returning on the neutral? Since we do not know for fact, it is an assumption either way would it not be?

Non-linear loads put harmonic currents on the supply circuit. In particular, it is the 3rd harmonic and other multiples of 3, that matter most. 180 Hz when 60 Hz is the nominal frequency, and multiples thereof.

Unlike the fundamental 60 Hz currents that add up to zero when loads are balanced, 3rd harmonic currents and subsequent multiples accumulate constructively on the neutral, even if the three phases are balanced. So when these harmonic currents are significant, the neutral carries enough current to generate heat, even with balanced phase conductors.

Can anyone speak to how you would quantify the 50% nonlinearity of a mix of loads? In otherwords, what would I look for on a datasheet, and how would I add up the value for all loads in a given panelboard?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Non-linear loads put harmonic currents on the supply circuit. In particular, it is the 3rd harmonic and other multiples of 3, that matter most. 180 Hz when 60 Hz is the nominal frequency, and multiples thereof.

Unlike the fundamental 60 Hz currents that add up to zero when loads are balanced, 3rd harmonic currents and subsequent multiples accumulate constructively on the neutral, even if the three phases are balanced. So when these harmonic currents are significant, the neutral carries enough current to generate heat, even with balanced phase conductors.

Can anyone speak to how you would quantify the 50% nonlinearity of a mix of loads? In otherwords, what would I look for on a datasheet, and how would I add up the value for all loads in a given panelboard?
If you are looking for a rule you can blindly apply, I have nothing for you.
But if the equipment gives a Total Harmonic Distortion figure for the load current, I would say anything less than 50% would be reassuring.
If they gave specific figures for each harmonic, it would be even better.
 

mjmike

Senior Member
What would be non-linear; no current returning on the neutral? Since we do not know for fact, it is an assumption either way would it not be?

Just to clarify this, I understand what non-linear loads are. I was asking what loads would one assume for a residential project would not be considered non-linear?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Just to clarify this, I understand what non-linear loads are. I was asking what loads would one assume for a residential project would not be considered non-linear?
Given modern energy and interference requirements for lights, for TVs, and for computer power supplies, I would have to say very little.
Very old computers, very old CFLs, maybe.
Cell and other chargers, maybe, but the wattage is so low that I would ignore them.
Possibly inverter type heat pumps, but very unlikely there too.

There are far more opportunities for non-linear loads in a commercial/industrial environment.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
A good portion of the load in a residential building is 3Ø elevators, fans, pumps, heaters, etc. IMO there are no real sizable harmonic loads that would get you near the 50% threshold.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
A good portion of the load in a residential building is 3Ø elevators, fans, pumps, heaters, etc. IMO there are no real sizable harmonic loads that would get you near the 50% threshold.
99% of what I get involved with is industrial now, but I just did some volunteer work at an applicable project this week. It's a managed care facility, mostly developmentally disabled people so the 18 individual living units do not have stoves or ovens. The heat and water heater system is all gas and the commercial kitchen is all gas cooking. The electric loads are the elevator, which has a VFD on it (I was the one to discover that so I know for sure), the 2 Air Handlers, which is where they are wanting to ADD new VFDs, and the plugs and lights. All of the 18 rooms have TVs plus a giant screen system in the entertainment room, they estimated that almost all of the residents have some sort of gaming system hooked up to the TVs and some sort of music system, most of them have PCs or tablets, and all of the lighting is either Fluorescent, CFL or LED. The only significant electrical loads I found that were linear were the 2 large commercial refrigerators and a freezer (the laundry is off site). My estimate was 90% non-linear loads! It was kind of an eye opener really.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
99% of what I get involved with is industrial now, but I just did some volunteer work at an applicable project this week. It's a managed care facility, mostly developmentally disabled people so the 18 individual living units do not have stoves or ovens. The heat and water heater system is all gas and the commercial kitchen is all gas cooking. The electric loads are the elevator, which has a VFD on it (I was the one to discover that so I know for sure), the 2 Air Handlers, which is where they are wanting to ADD new VFDs, and the plugs and lights. All of the 18 rooms have TVs plus a giant screen system in the entertainment room, they estimated that almost all of the residents have some sort of gaming system hooked up to the TVs and some sort of music system, most of them have PCs or tablets, and all of the lighting is either Fluorescent, CFL or LED. The only significant electrical loads I found that were linear were the 2 large commercial refrigerators and a freezer (the laundry is off site). My estimate was 90% non-linear loads! It was kind of an eye opener really.

Just how non-linear (in terms of distortion power factor) was the total load?
 