The #14 pigtail restriction is another of Code things that I understand what the intention is, but the reality is I feel there is no real safety issue with a #14 pigtail, even with a load of 20 amps continuous.
How do I know this?
Many years ago the EC I worked for and I set up a test..we set up a test rig, with receptacles, one wired with #12 pigtails (8 inches long) and the other with #14 pigtails 8 inches long.
We taped thermocouples to each pigtail to measure the ultimate temperature.
We then mounted each receptacle in a standard box, put on cover plates and applied space heater loads at 20 amps each.
I do not recall the exact temperatures we got, but neither got more than 10-15 degrees f above ambient, and the difference between the #14 and #12 was only about 10 degrees f. But all temperatures were well below 60c after conversion from f.
The point is there was no significant temperature rise with a #14 pigtail. This was after 3 hours of non-cycling load.
So from a safety standpoint I see no problem with it.
But as long as Code requires it, #12 on #12 is what I will do.
Anybody use the wirenuts with white and black pigtails attached to them? I have and they worked well, but would be expensive for use on large jobs.
How do I know this?
Many years ago the EC I worked for and I set up a test..we set up a test rig, with receptacles, one wired with #12 pigtails (8 inches long) and the other with #14 pigtails 8 inches long.
We taped thermocouples to each pigtail to measure the ultimate temperature.
We then mounted each receptacle in a standard box, put on cover plates and applied space heater loads at 20 amps each.
I do not recall the exact temperatures we got, but neither got more than 10-15 degrees f above ambient, and the difference between the #14 and #12 was only about 10 degrees f. But all temperatures were well below 60c after conversion from f.
The point is there was no significant temperature rise with a #14 pigtail. This was after 3 hours of non-cycling load.
So from a safety standpoint I see no problem with it.
But as long as Code requires it, #12 on #12 is what I will do.
Anybody use the wirenuts with white and black pigtails attached to them? I have and they worked well, but would be expensive for use on large jobs.