SIZE TRAMSFORMERS
Re: SIZE TRAMSFORMERS
Voltage * current * sqrt (3) = size.
The voltage is line to line. Currrent and voltage should both be RMS, both from the same side of the transformer (use 480V and 1200A).
Then add any extra spare capacity that might be prudent.
Steve
If you want to use single phase transformers use three 333KVA single phase transformers configured delta-wye. 13.800 KV primary delta and 480/277 secondary. These three will give you 1200 amps on the secondary.