Yes, I understand why they want a small tranny. My demand is about like a larger household maybe, I have a 3hp well and my biggest walk in cooler is 3 hp although not currently using it as I have a 1 also and while I have 5 hp comp to meet demand or backup rarely use that as I have 3 with 200 gallons on it. Same foir welding, have a 300 synch I never use and the rest is factory cord common 50A service with about 40 peak with that and very intermit with 1/2 that on machine uses 23 or less. Just no big cruncher loads,
It would be interesting to see what the peak was, pressure wash at 5 hp when the cooler was running, well and air comp on a small ac in office, wonder if it ever hit 100 and for how long?
Max,,, maybe 3 or 4 minutes under extreme circumstances a time or 2 over decade.
The assumption about demand is wayyy off with the speculators. The diy forum has many like,,,, should I upsize to 10 for my loooooooooooong run,,, almost 25 ft and I might use a 4 1/2 grinder and a light bulb at the same time and what if my bro in law is standing there with a beer,,, well then my load will rocket. Its really hard concept especially with general circuit to grasp because it has a 20 breaker and 100 ft of wire that isnt actual load, first recept 15 ft away is doing 90% of the work so we worry about v drop on the other end for 20A and 1 lamp or zing with a circ saw.
In the end 200 would have been dandy and would have simplified any backup power, 2 panels 1 meter base is a problem.
Given the nature of my buildings etc would have figured 25k if I was doing the calc but its never been a problem.
I did make a move with the pole that required a wire change and I actually negotiated with the engineer at plan review over the conductor size and the lineman made a comment about it,,, the old wire would have been fine but was now 10 short and they bring a new wire in,, and was 500 mcm maybe where the old might have been 2/0, its been a while now.
I figured efficiency but hadnt occurred to me especially at the time about fault current, its a long rural line single phase, 14000 I believe. They had 10hp limit till recent soft starts, not sure what it is now.