Ungrounded Feeder Conductors
The conductors must independently meet requirements for (1) terminations, and (2) conditions of use throughout the raceway run.
Minimum size conductor at the overcurrrent device termination [see 110.14(C) and 215.2(A)(1), using 75°C ampacity column in Table 310.15(B)(16)]: 1/0 AWG.
Minimum size conductors in the raceway based on actual load [see Article 100, Ampacity, and 310.15(B)(3)(a) and correction factors to Table 310.15(B)(16)]:
95,500 VA / 0.7 / 0.96 = 142,000 VA [70% = 310.15(B)(3)(a)] & [0.96 = Correction factors to Table 310.15(B)(16)]
Conversion to amperes: 142,000 VA / (480V × √3) = 171 A