Check with the AHJ
Check with the AHJ
Not sure how it is done in Texas, but in California, the AHJ for all Manufactured Modulars/Trailers is HCD (Department of Housing and Community Development). HCD states that the Nameplate rating is what must used for Modulars/Trailers. So even if the Load is only 60 Amps, the Service (and SE conductors) must be capeable of handling the Nameplate rating (usually 125 Amps per section).
I could be wrong (if so it wouldn't be the first time today). Hope that this helps.
Check with the AHJ
Not sure how it is done in Texas, but in California, the AHJ for all Manufactured Modulars/Trailers is HCD (Department of Housing and Community Development). HCD states that the Nameplate rating is what must used for Modulars/Trailers. So even if the Load is only 60 Amps, the Service (and SE conductors) must be capeable of handling the Nameplate rating (usually 125 Amps per section).