I have a 100hp pump panel fed by #2 thhn wire. The contacter has heaters and there is a 300 amp mag break circuit breaker in the pump panel - so far, so good. (Motor is protected)
The circuit breaker that I would like to use to feed this pump panel and protect the #2 wire is a GE TED136150 (150 Amp thermal magnetic breaker)
The breaker looks very small compared to the breaker in the pump panel......
I assume the small size has to do with its AIC rating which is 18ka.
There is no way to adjust the mag trip on this breaker, am I using the wrong style of breaker?
Thanks for any help
The circuit breaker that I would like to use to feed this pump panel and protect the #2 wire is a GE TED136150 (150 Amp thermal magnetic breaker)
The breaker looks very small compared to the breaker in the pump panel......
I assume the small size has to do with its AIC rating which is 18ka.
There is no way to adjust the mag trip on this breaker, am I using the wrong style of breaker?
Thanks for any help