Hello,
I am wiring an above ground pool for a friend, the nameplate on the pump is 10.5a @ 120v and the heater is 42a @ 240v. So to calculate: (120*10.5 = 1260w) + (240*42 = 10080w) = 11340w. Both would be considered a continuous load so: 11340*1.25 = 14175w. Then 14175/240 = 59a. At this point I figured I would protect this feeder with a 60a breaker and run 6/3 mc across my friend's unfinished basement, then change over to #6 thhn before going outside and underground out to a pool panel. However, I will also run the convenience receptacle out of this pool panel. Would that force me to go up to a 70a breaker and feeder, 4/3 romex, and #4 thhn?
I am wiring an above ground pool for a friend, the nameplate on the pump is 10.5a @ 120v and the heater is 42a @ 240v. So to calculate: (120*10.5 = 1260w) + (240*42 = 10080w) = 11340w. Both would be considered a continuous load so: 11340*1.25 = 14175w. Then 14175/240 = 59a. At this point I figured I would protect this feeder with a 60a breaker and run 6/3 mc across my friend's unfinished basement, then change over to #6 thhn before going outside and underground out to a pool panel. However, I will also run the convenience receptacle out of this pool panel. Would that force me to go up to a 70a breaker and feeder, 4/3 romex, and #4 thhn?