Where is the #3 AWG cable coming from, I come up with #6AWG.
Thanks,
Accounting for 3% voltage drop.
The MCA is 15 amps, so I multiplied by 125% to get 18.75amps. So I size the wire to withstand 18.75amps for a distance of 1500, gives me #3 using mike holt spreadsheet.
But just reading from other posters, i don't need to add additional 125%, just the 15amps cause thats straight from UL nameplate data.
So just using 15amps, I get #4 size wire.
My fuses will be 15amps based on the MOCP at my MCC bucket. Looks like I am done! I hope so:?