I have to run some underground over to a remote distribution panel in a house. My plan is to set a j box on the rim joist and want to make sure I have it sized correctly.
I will be running - 1/0,1/0,1/0 aluminum triplex with a #8 copper egc inside of 2”pvc from 100 amp breaker inside a 200a service disconnect to a 16”x16”x6” j box. I planned on punching a hole in the rim joist coming out the back of the box with a connector and switching to 1/0,1/0,1/0,#2 ser aluminum and getting it inside the existing 100amp panel through the crawl space…
This will be and angle pull with 2” being the largest raceway
I believe 314.24 explains the j box doesn’t need to be bigger than 6x the largest raceway entering the box. So my minimum size would be 6x2”=12”
Looks like I could use a smaller box but don’t want to have trouble putting the cover on. Does this seem like I have an accurate understanding or have I missed something ?
Any and all help is appreciated greatly thanks!
I will be running - 1/0,1/0,1/0 aluminum triplex with a #8 copper egc inside of 2”pvc from 100 amp breaker inside a 200a service disconnect to a 16”x16”x6” j box. I planned on punching a hole in the rim joist coming out the back of the box with a connector and switching to 1/0,1/0,1/0,#2 ser aluminum and getting it inside the existing 100amp panel through the crawl space…
This will be and angle pull with 2” being the largest raceway
I believe 314.24 explains the j box doesn’t need to be bigger than 6x the largest raceway entering the box. So my minimum size would be 6x2”=12”
Looks like I could use a smaller box but don’t want to have trouble putting the cover on. Does this seem like I have an accurate understanding or have I missed something ?
Any and all help is appreciated greatly thanks!